I need help (KVA)

Hi,

I would like to know the Kva for the following appliances.

4 freezers at 5 amps each

3 chiller units at 3 amps each

2 chillers at 35 amps each.

I do not know if they are resistive or conductive(if that is necessary for the answer)

Would the answer be 79 * 240 /1000 = 18.96??

Hope you can help.

Confused

Reply to
george
Loading thread data ...

If all you appliances are running off of 240 you're almost correct... you for got to add in the 4 freezers so add 20 more amps and you should come up with 23.76kVA

Reply to
GotCoffee

That is an upper limit - assuming all are running at the currents given and all are at the same power factor.

--
Don Kelly
dhky@peeshaw.ca
remove the urine to answer
>