Are there any solid-state devices to convert 240 v 1 phase to 415 volt
3-phase ? Available in the UK ? I would like to run a small (1/8 hp) 415 volt 3 phase motor from the 240 volt single phase supply.Jim Hawkins
Are there any solid-state devices to convert 240 v 1 phase to 415 volt
3-phase ? Available in the UK ? I would like to run a small (1/8 hp) 415 volt 3 phase motor from the 240 volt single phase supply.Jim Hawkins
A variable frequency drive rectifies the single (or 3 phase) line power into DC, then constructs 3 phases of AC from the DC supply, usually with a PWM modulation method. But this produces an AC output voltage about as high as the AC input voltage, so if you cannot reconnect the motor for lower voltage operation, you would need a 3 phase step up transformer between the drive an the motor, also.
Here is an example of this kind of drive:
-- Regards, John Popelish
A variable frequency drive (VFD) such as
-Lasse
Real "old school" way to do this would be to use a transformer to step up to 415 volts, and then a good sized "starting" capacitor to do a fairly bad job of synthesizing phase lag to power 3rd phase lead on motor. Efficiency isn't nearly so good as with modern solid state drives, but, it's cheap, and you see lots of old machine tools and other gear with 3 phase induction motors run that way, hooked to single or two phase mains....
W Letendre
drive:
assuming it is "normal" european 3-phase the 415V is between phases, each phase to neutral is still only 240, so not step up should be needed
-Lasse
I know you asked for solid state but rotary is cheap:
1.5kW for £490 fromThe good thing about rotary converters is that they are *much* more tolerant of short term overload.
Michael Kellett
Bit overkill for 1/8 hp though ! I've just found this on eBay:-
Thanks to all for your information and interest.
Jim Hawkins
ElectronDepot website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.