I can't seem to find an answer to this question anywhere, So I've come to the experts. I need to power a device that requires 500ma of
12v dc current, but it has to be 200 feet away from the transformer. Will a 1amp power supply provide adequate current over a 14 gauge wire? Is there a formula to figure this out? Thanks in advance
Nick (servozoom)
Didn't find your answer? Ask the community — no account required.
P
purplefloyd
Thanks so much to everyone, outstanding info, John's chart is a keeper, and Figaro's calculation made my job much less painless. You guys are the best.
J
John Popelish
You can find many tables of wire data through Google, like this one:
formatting link
It lists the ohms per 1000 feet (ohms /Kft) and feet feet per ohm for many wire gauges. You should be able to apply Ohm's law to some possibilities and figure out how much of your 12 volts will get lost in the wire, out and back.
D = 400 feet (200 feet x 2 round trip) I = 0.5 amps R = 2.575 ohms per 1000 feet
then V = 0.52 volts = voltage drop
your power supply must be 12.52 volts so that the voltage at the far end device will be 12.0 volts
S
servozoom
Thanks for all the info, I understand the problem much better.
M
me
Oh boy, where do we even begin:
This question is impossible to answer because you don't provide useful information. First there's a question of your power source and then there's a question of your load.
You claim you are 200 feet away from the transformer and then talk about a 1 amp power supply. So do you mean a 1 amp wallwart? You can't put DC into a transformer so you'd have to rectify it on the output of the transformer, it would also be a good idea to regulate it. You also don't state what voltage is acceptable at the load. 12V +/- what? Bare in mind that wallwart voltage tends to go all over the place depending on the load and they are unregulated.
14 gauge wire has a resistance of .00297 ohms per foot (assuming copper wire, and room temperature, resistance goes up with temperature), so 200 feet of it * 500mA gives you about .3V of drop. That means the voltage at the output of the transformer must be at least .3V above what you need at the load.